Balancing the
Control of Heat, Air, Moisture, and Competing Interests
By:
Patrick J. Roppel,
Mark D. Lawton, & Brian Hubbs
INTRODUCTION
The premature
deterioration of multi-unit residential buildings in the Lower Mainland
of BC due to rainwater penetration has been well documented in the past
10 years (Morrison Hershfield 1996, RDH 2001, Lawton 2004).
Consequently, rehabilitation designs for such buildings focus on
eliminating rainwater penetration as a damage mechanism.
Typically, these
buildings are more air tight after rehabilitation than they were
before. This has the benefit of not only eliminating potential paths
for water ingress but also reduces the amount of heat loss through and
potential for condensation within the building envelope. Mechanical
ventilation is important to the performance of an airtight building, as
adequate ventilation is necessary to maintain a healthy and comfortable
environment for occupants. Without adequate ventilation, the occupancy
may cause the relative humidity to rise to a level where, depending on
the wall design and climate, condensation will form on the windows or
interior drywall, or within the wall assembly itself.
Moisture is the
single leading cause of deterioration of building envelope materials.
Moisture from the exterior, e.g., rainwater, if not restricted, can lead
to premature deterioration of building materials. The path for
rainwater penetration is usually a consequence of inadequate design or
construction details. Conversely, wetting by moisture transported from
the interior environment is typically a slower damage mechanism. The
source of wetting from moisture transport from the interior is sometimes
more difficult to determine in the field since damaged areas are a
consequence of the combined heat, air, and moisture flow in four
dimensions, time being an important factor in both the duration of
accumulation and the onset of deterioration. If a wall has suffered
severe deterioration due to rainwater penetration, then the challenge
for rehabilitation projects is to determine whether there is damage by
wetting from vapour diffusion from the interior as such damage may be
masked by the severity of deterioration by rainwater penetration. After
rehabilitation, with a more airtight envelope, the balance interior
humidity levels may be difficult to ascertain.
This paper draws on
one rehabilitated wall assembly in Vancouver, B.C. as an example to
illustrate the importance of balancing the control of heat, air, and
moisture flows from both the interior and exterior. The primary cause
of premature envelope failure was determined to be rainwater
penetration, and the interior humidity was identified as a problem that
required corrective action.
The rehabilitated
exterior walls consist of a rain-screen stucco wall assembly with 50 mm
of semi-rigid mineral wool insulation, self-adhering SBS-modified
bitumen membrane on fiberglass faced gypsum sheathing, 90 mm steel studs
with fiberglass batt cavity insulation, and interior drywall with latex
paint.
Eight exterior wall
cavities and two suites were instrumented with sensors on the east
elevation during the rehabilitation of the building as part of a
monitoring project (Finch et al 2006). This monitoring project revealed
that moisture was collecting in the gypsum sheathing in winter. In
addition, mold growth was present on the interior surface of the drywall
on the exterior walls and excessive condensation was occurring at the
aluminum windows. These symptoms were attributed to condensation due to
the high interior relative humidity in the building.
A follow-up
investigation was undertaken to address the concerns raised by the
monitoring program and to determine the following:
·
The
level of ventilation provided by the existing mechanical systems.
·
The
effectiveness of the provided level of ventilation with respect to
control of interior humidity, other contaminates, and moisture
collection in materials in the wall assembly.
·
What
changes to the ventilation strategy will provide appropriate control of
interior humidity, other contaminates, and moisture collection in
materials in the wall assembly.
·
Alternative methods of increasing tolerance of the wall assembly for
high humidity levels.
The intent of this
paper is to discuss how the rehabilitated wall assembly compares to
current design practice to identify how the building operation and
performance can be improved for future rehabilitation projects.
THE INDOOR
ENVIRONMENT AND BUILDING OPERATING CONDITIONS
Both exterior and
interior environmental design loads must be considered when designing a
wall assembly to control heat, air and moisture flows. Exterior
environmental loads such as temperature, precipitation, solar radiation
and humidity can be determined from climatic data. Interior moisture
loads are comparatively more complex to establish for buildings with
uncontrolled humidity since the indoor humidity is a function of the
outdoor vapour pressure, ventilation rate, moisture generation rate, and
absorption/desorption of interior hygroscopic materials (Roppel et al
2007).
Ventilation controls
the interior vapour pressure by exchanging moisture-laden air with
exterior air, which in cool climates is typically at a lower vapour
pressure. The rate of moisture generation and the control of
ventilation and temperature of each suite in a multi-unit apartment
building all have an impact on the interior humidity.
Air that is removed
from a suite by an exhaust fan will be replaced with air that originally
came from the exterior. The path of the air flow will be:
·
directly from outside through the envelope or an exterior make-up air
supply,
·
via
the corridor pressurization system through the corridor and through
intentional or unintentional openings (i.e., door undercuts) in the
suite demising walls,
·
from
adjacent suites, carrying moisture and contaminated air generated in
those suites.
The following
sections identify the key parameters governing the indoor operating
conditions. Typical design assumptions are compared to actual operating
conditions as determined from field measurements.
Principal Exhaust Ventilation Rate
The suites of this
building have individually ducted bathroom fans that have been provided
(following rehabilitation) with time-activated switches according to the
concept of the principle exhaust fan required under Part 9 of the
current Vancouver Building Bylaw (VBBL) and the British Columbia
Building Code (BCBC). The timers are located in lock boxes which
minimizes tampering but complicates adjustments for conditions or to
corrections for time changes or power outages.
The airflow of the
fans was measured with a flow hood under four different conditions:
1. With all windows
and the suite entry door closed and the bathroom door open;
2. With all windows,
the suite entry door, and the bathroom door closed;
3. With all windows
closed, the suite entry door cracked open and the bathroom door open;
4. With a window
cracked open, the suite entry door closed and the bathroom door open.
Table 1 shows the
measured flow of the bathroom flow rates in the first condition and
compares that with the requirements of the current VBBL.
There was relatively
little difference in the four measurements (less than 5 CFM). Air
tightness of the suites did not seem to affect the exhaust rate of the
bathroom fans (it would affect where the replacement air was drawn
from). This indicates that the flow rate is limited primarily by the
resistance of the in-slab duct that services the bathroom fans.
The current VBBL and
BCBC have similar minimum requirements as ASHRAE Standard 62 which
recommends 15 cfm/ person. Table 9.32.3.3.A requires a minimum
ventilation rate for the principal exhaust, which may be the bathroom
exhaust fan, based on the number of bedrooms. The VBBL requires that
the principal exhaust fan be controlled by an adjustable time control
device to provide a minimum of two 4-hour operating periods per day, or
be designed to run continuously.
A separate
requirement states that the bathroom fan should have a capacity of 50
CFM if run intermittently or 20 CFM if run continuously.
Table 1:
Bathroom Fan Operation (Condition 1)
|
Suite |
Number of
occupants |
Number of
Bedrooms |
Estimated
fan operation time (hours) |
Flow Rate (CFM) |
VBBL
Capacity Requirement (CFM) |
15 CFM /
Person (CFM) |
|
201 |
4 |
3 |
N/A |
36 |
60 |
60 |
|
205 |
4 |
2 |
2 |
37 |
45 |
60 |
|
208 |
2 |
2 |
12 |
38 |
45 |
30 |
|
211 |
3 |
2 |
4.5 |
58 |
45 |
45 |
|
302 |
5 |
3 |
5 |
35 |
60 |
75 |
|
308 |
2 |
2 |
N/A |
42 |
45 |
30 |
|
309 |
4 |
3 |
1 |
42 |
60 |
60 |
|
311 |
3 |
2 |
6 |
44 |
45 |
15 |
|
409 |
5 |
3 |
4 |
46 |
60 |
75 |
|
505 |
2 |
2 |
12 |
55 |
45 |
30 |
|
511 |
3 |
2 |
4 |
20 |
45 |
45 |
|
602 |
4 |
3 |
6 |
61 |
60 |
60 |
|
608 |
4 |
2 |
N/A |
41 |
45 |
60 |
|
611 |
2 |
2 |
<1 |
50 |
45 |
30 |
The range of
measured values is 20 to 61 CFM, with an average rate of 43 CFM. From
questioning the occupants of the suites, it appears that the fan timers
were not set to the same time or to meet the expected peak moisture
production or the code defined duration (two – 4 hour periods).
As can be seen in
Table 1, four of 14 fans (29%) meet the minimum capacity as outlined in
the current VBBL and two of 11 (18%) appear to be operating the minimum
duration.
Many of the bathroom
fans were noisy (subjective opinion), and the noise level was identified
by the occupants in Suite 611 as a contributing factor to lack of use of
the bathroom fan. The noise levels of the fans were not measured, but
the VBBL states that the principal exhaust fan should have a 1.5 Sone
sound rating when controlled by an adjustable timer or 1.0 Sone when
operating continuously.
Make-up Air and Fresh Air
The building had no
provision to deliver fresh make-up air directly to the suites.
Therefore, make-up air will likely be drawn from a combination of the
corridors, adjacent suites and the exterior walls. The path of air
exchange is dependent on the relative size of openings and pressure
differentials between the suite and adjacent zones (corridor, adjacent
suites, exterior environment).
The corridor fan
flow was measured, the unobstructed opening under the suite entry doors,
and the pressure difference from the suite to the corridor, to establish
how much fresh air could be expected to be delivered to each suite from
the corridor. Tables 2 and 3 summarize the measured data.
Table 2:
Measured Corridor Fan Flow Rates (CFM)
|
Floor Level |
Corridor 1:
Suites
1 to 6 |
Corridor 2:
Suites
9 to 12 |
|
6 |
390 |
246 |
|
5 |
291 |
311 |
|
4 |
517 |
313 |
|
3 |
125 |
272 |
|
2 |
215 |
467 |
Table 3:
Suite Entry Door Measurements
|
Suite |
Height of
Space under Door (mm) |
Pressure
Difference measured between Corridor and Suite |
|
201 |
13 |
0 |
|
205 |
2 |
1 |
|
208 |
13 |
2 |
|
211 |
13 |
1 |
|
302 |
5 |
2 |
|
308 |
0 |
-1 |
|
309 |
10 |
-2 |
|
311 |
13 |
0 |
|
409 |
13 |
0 |
|
505 |
0 |
-1 |
|
511 |
13 |
0 |
|
602 |
13 |
2 |
|
608 |
0 |
0 |
|
611 |
0 |
0 |
A minimum capacity
of 330 CFM for the corridor 1 supply (6 suites in total) and 210 CFM for
corridor 2 supply (4 suites in total) is sufficient to supply the volume
of air that would be exhausted if a principal exhaust fan, meeting the
code defined minimum flow rates, was on for all of the connected
suites.
Generally, it
appears that sufficient fresh air is being supplied to the corridors
(but is not necessarily getting to the suites).
A positive pressure
difference measured from the suite to the corridor indicates that the
pressure in the corridor is greater than the pressure in the suite.
When the bathroom fan is running, make-up air will travel under or
around the suite door at a rate dependent on the open area. Fresh air
from the corridors is restricted by door sweeps installed in many
suites. For the measured pressure differences and opening areas, the
expected flow rate from the corridor is approximately 5 to 25 CFM, which
represents 15% to 60% of the bathroom fan exhaust rate.
A large amount of
the make-up air for individual suites may be from adjacent suites. This
route is likely since the bathroom exhaust fans in each suite appear to
be operating at different times and durations.
Carbon dioxide (CO2)
levels were measured as an alternative method of assessing whether
adequate ventilation is provided with the current building operation.
The ASHRAE Handbook of Fundamentals (2005) states that CO2 is
not normally considered to be a toxic air contaminant but high levels
are associated with symptoms such as increased headaches and reports of
people feeling tired. Measuring CO2 can be used as a method
of evaluating the level of ventilation. Outdoor CO2 is
typically in the range of 330 to 370 ppm or slightly higher in urban
environments due to automobile emissions. A level of 1000 ppm has been
suggested as being representative of a CO2 concentration when
fresh air is being delivered at the ASHRAE’s recommended 15 cfm per
person.
A summary of single
point CO2 measurements taken during the day when site visits
were carried out is found in Table 4. Many suites had their windows
open before arrival to take measurements; therefore, the lower readings
are indications of the exterior ambient CO2 levels. The
lowest reading was 382 ppm, which is in line with the typical value
stated by ASHRAE Handbook of Fundamentals (2005). Four of the 13 suites
(31%) measured had readings above 1000 ppm.
Table 4:
Suite CO2 Measurements
|
Suite |
CO2
(ppm) |
|
201 |
1135 |
|
205 |
1183 |
|
211 |
|