Building Air Barrier Testing and Verification Using Smoke Flow Testing and Infrared Thermography in the Canadian Arctic: A Case Study - 2002-2003By: Richard Ogle & Bill WynessIntroduction This paper summarizes the techniques used to verify and correct air tightness of the building envelope in the new Inuvik Regional Health and Social Services Centre, a recently commissioned $40 million dollar facility in the high arctic. Since the 1980’s the requirement for air-barrier continuity of building envelopes has become increasingly recognized. Part 5 of the National Building Code of Canada (NBCC 1995) Environmental Separation requires that wherever a building assembly separates an interior conditioned space from an exterior space that it contain an air barrier system. The air-barrier system is required to be continuous, be durable through mechanical support, and conform to stipulated air leakage rates based on the use of low permeability materials and joints between those materials. Uncontrolled air leakage can cause condensation problems, increase energy consumption and adversely affect occupant comfort. The need for an effective air barrier system is particularly acute in Canada’s Arctic where environmental loads are harsh and maintenance and operating costs are high. Inuvik has a 2-1/2% January design temperature of –46 oC and averages 10,050 Degree Days Below 18 oC. For comparison, Calgary has a 2-1/2% January design temperature of –31 oC and averages 5200 Degree Days Below 18 oC. Case Study BuildingThe Inuvik Regional Health and Social Services Centre was constructed in the years 2001 through 2003. Figures 1 and 2
Figure 2: The exterior wall system consists of a structural insulated panel system. The project delivery method was a negotiated, fast-tracked design-build model, where the Project Manager, Ninety North Partners, consisting of Ninety North Construction and Stuart Olsen Construction retained the project design consultants, Stantec. Technical performance requirements stipulated for the facility by the Owner included the NBCC 1995, applicable technical standards for Canadian health care facilities, and recommendations from Good Building Practice for Northern Facilities, a recommended best practices document developed by the GNWT after ten years of technical performance evaluation of buildings throughout the NWT. Since this is a health care facility, the minimum interior relative humidity was required to be 30% and the building was required to be positively pressurized by the air handling system. These are considered rigorous environmental loads for a building envelope in such a cold climate. The plan area of the facility is approximately 8000 m2 with an irregular shaped floor plan. The roofs are low-slope with a 2-ply SBS modified bitumen water shedding membrane in a conventional configuration. The walls are constructed of 100 mm thick structural insulated panels (SIPS). Each panel consists of a pre-fin-ished metal facer bonded to a urethane insulation core. The panels interlock and seal on the vertical edges by means of a tongue & groove type of profile, and field applied sealant in the joint between the panels, with a modified bituminous membrane (MBM) facing strip on the interior panel face. Figure 3. The panels rely for the air-barrier seal at the top and bottom on correctly installed low-permeance materials bridging from the panel face to the roof air-barrier system and the crawl-space air barrier system at the panel base.
Figure 3 The SIPS panels consist of a 100 mm thick urethane foam core with metal facers and interlocking edges. The SIPS wall system was selected because of its light shipping weight, high insulating value, rapid deployment to quickly enclose the building during the short arctic construction season, and lateral load resistance. However there were some concerns with the use of this system with respect to continuity of the air barrier, particularly at locations such as wall-to-roof junctions, window connections, panel-to-panel joints and wall-to-base support junctions. A typical wall section and details of the parapet and grade level panel joints are presented in Figures A1 through A3 in the Appendix. Smoke Testing As wall panel installation proceeded, air barrier continuity was checked using smoke testing. The technique involves creating a pressure difference across the air barrier system and then using a portable smoke generator to identify breaks. Since the building was not completely closed in and the mechanical system was not operational, the pressure difference had to be created by means of a variable speed portable fan. Figure 4. Small areas of the exterior walls were enclosed with gypsum board and polyethylene sheets and then pressurized to approximately 25 Pa with the fan. Smoke was sprayed at critical joints and details on the interior while observations were made on the exterior. Walkietalkies facilitated communication.
Figure 4 Air pressure differences were achieved in sections of the partially completed building using a blower door fan (right). A smoke generator (above) was then used to identify typical air leakage paths.
An effort was made to have representatives of all interested parties present during the testing. This included representatives of the owner, project manager, subcontractors, design consultant and building envelope consultant. Although air tightness requirements are often specified in terms maximum air flow rates per unit area of wall at a given pressure difference, it is seldom practical to conduct quantitative tests in the field to verify these figures. It is therefore important to understand that on this project the smoke testing was strictly qualitative in nature. Once a discontinuity was identified using smoke, the leakage path was confirmed by visual inspection. No flow rate measurements were made. As a result of the smoke testing the following major air leakage paths were identified: a) Roof to panel junction; b) The base of the panels near grade level; c) The roof to wall curb on the second floor; d) some vertical panel to panel joints. Following the smoke testing the general contractor and the sub-contractors began a program of air barrier remediation. This mainly consisted of using sprayed urethane foam and caulking to seal various joints throughout the building. Infrared Thermography – General ConceptsAlthough smoke testing readily demonstrates typical air barrier discontinuities, it is difficult to verify the air tightness of the entire building envelope of a large facility using this technique. Positive building pressure cannot be achieved until the building’s mechanical system is operational. By that time, the inside surface of the building envelope is usually covered by various interior finishes. Furthermore, the sheer surface area involved makes complete smoke testing impracticable. Infrared thermography has been used to identify building envelope deficiencies for over thirty-five years. Thermography relies on the physics principle that objects emit a frequency of electromagnetic radiation in proportion to their absolute temperature. In the case of objects which are at terrestrial temperatures, this radiation turns out to be beyond the visible spectrum, and is called infrared i.e. “below” red in the visible spectrum. Thermographic cameras use sensors to measure the infrared light and create a visible image based on an electronic mapping of the infrared light to the visible spectrum. Modern thermographic cameras can display infrared images in a variety of chromatic schemes. Besides producing a visible image, the absolute temperature at any point in the image can be determined. A so-called ‘spot temperature’ can be identified by the camera for the reference cross hairs in Figure 5.
Figure 5 The thermographic image (thermogram) on the right shows air leakage at the base of the SIPS panels at grade level. Note the snow on the flashing is melted where the air leakage is most intense. One important feature of thermography is that large areas of the building can be surveyed in a relatively short period of time. Usually one session under optimal conditions (the absence of solar spectral radiation and the absence of excessive exterior winds) is sufficient to complete the entire survey and identify spots where the usual temperature of the surface is substantially varied. These variations are typically referred to as thermal anomalies, and are caused by conductive or convective heat migration through the building envelope. A second important feature is that the survey can be recorded both with still images and on videotape or DVD. Since the infrared images are read from the surface temperatures of the object, deficiencies other than air leakage are identified. These thermal anomalies include missing or improperly installed insulation and low thermal resistance pathways through the envelope, usually called thermal bridges. While infrared thermography can locate and measure temperature anomalies, it is not capable of determining the cause of a particular anomaly in a wall or roof assembly. The cause must usually be confirmed by physical verification, involving review of the construction detail, smoke flow testing to locate air leakage paths through the assembly, and opening up the assembly to precisely locate the failed air-barrier component. Initial Thermographic SurveyThe first thermographic survey was carried out in November 2002. Prior to carrying out the survey a proposed set of procedures and conditions was circulated for comment among the stakeholders. A meeting was then held at the site with representatives of the owner, general contractor, building envelope consultant and thermographer to confirm the survey procedure. Among the more important points that were arrived at were: • The thermographic survey would be carefully documented in terms of environmental conditions, viewing angles and anomaly locations. This would establish a benchmark, or reference, for future year thermographic surveys, a requirement of the owner.
Spot temperature measurements would be taken of apparent thermal anomalies and these temperatures would be compared to the ambient viewframe temperature. Based on previous experience, it was suggested that a temperature difference on the building surface of greater than 10oC was indicative of a very significant anomaly.
It was agreed that the definition of what constituted a deficiency would likely require some physical investigation after the survey was complete.
The outside air temperature at the time of the 2002 survey was approximately –17 oC, the inside temperature was 21 oC and wind was calm. These conditions are considered suitable for producing good thermal images. The building was pressurized to a target pressure of approximately 35 Pa using the mechanical system. Positive pressurization was essential for causing exfiltration of warm interior air through the envelope during the whole period of thermographic surveying. Over ninety-five documentation sheets were prepared. The documentation sheets and the videotape of the survey were reviewed and physical investigation of the as-built construction was carried out. A typical documentation sheet is presented in Figure A4 of the Appendix. It was concluded that the following types of thermal anomalies due to air leakage were significant deficiencies: Some locations at the panel base at grade, Figure 5.
Some locations at the roof to wall junction, Figure 6.
Some locations at the roof to wall curb on the second floor level, Figure 7.
Some locations at panel joints, Figure 8.
Miscellaneous penetrations, Figure 9.
The sealant bead between insulating glass units and the window frame.
Figure 6Significant air leaks are apparent at two locations at the parapet. A minor leak can be seen in a panel seam on the right.
|
|
![]() |
Building Envelope Forum is published by York Communications/MMPI, the owners of the Construction Law Update News Bulletin, Canadian Apartment Investment Report, and Real Estate Forum. York Communications also produces Canada’s largest expositions and conferences for design, construction, and real estate management professionals including Construct Canada, HomeBuilder & Renovator Expo, Concrete Canada, PM Expo, DesignTrends, RoofTech and the Real Estate Forums. For more details, see our website at www.yorkcommunications.ca. |