|
The
Forum
Dear Ken
I read your article on Protection from Precipitation
Cladding Provisions in the Building Envelope Forum.
I am based in
New Zealand and
we have similar problems with leaky buildings as Canada does so the subject
is of interest.
You refer to a Two Plane System for certain claddings. In
New Zealand we have adopted a similar cavity drainage system for ventilation
and draining. This is formed by timber battens between the outer cladding
and building wrap on the timber framework.
My company has just developed and launched on the market
a polypropylene batten that has holes through it to drain or ventilate when
installed in a horizontal or vertical position. If you have a look on my web
page you will get a better understanding of it. www.cavibat.co.nz
It has numerous advantages over timber which are listed in the brochure
section.
The system has had independent testing at BRANZ a
division of NZ's department of Building and Housing
I am looking at the feasibility of bringing the batten
system to
Canada. You have obviously had experience in the building
arena and I would value your opinion as to the suitability of my system for
your construction industry in Canada.
Thanking you in anticipation, I look forward to your
response
Kindest regards
Graeme Webster
Managing Director
Cavity Batten Systems
graeme@cavibat.co.nz
http://www.cavibat.co.nz
Dear
Jacques Rousseau,
I loved this writeup, especially --
White’s First Law: The primary purpose of a Bureaucrat is to invent
reasons why things can’t be done.
[[ Tres applicable à la maison
blanche... ]]
Plus, this old house PPT show was an eye opener...
~!^)
- Bion
Contact Information
----------------------------
Mr. Bion D. Howard
Building Environmental Science and Technology
P. O. Box 23858
Hilton Head Island, SC 29925
Web: http://www.energybuilder.com
Dear
Jacques Rousseau,
I really enjoy
reading the various views of current construction techniques and the problems
and solutions expressed in the forum.
My quest for
something better over the last 20 years led me to build an ICF (insulated
concrete form) bungalow with a Can-am Hambro poured in place main floor. Both
the basement and the main floor have hot water radiant floor heat supplied
with a New York Thermal Infinity wall mount boiler.
The roof
trusses have a raised heel to allow full depth insulation to the outside
surface of the perimeter walls. There are no load bearing interior walls.
That made it easier to attach Nudura ceiling technology to the under side of
the trusses and completely drywall the ceiling before installing steel stud
interior walls.
Nudura ceiling
technology is 3.5” type 2 EPS foam with 1 X 3 wood molded into it on 16”
centers. Each pot light in the ceiling had a box installed fabricated from 2 “
extruded foam insulation and 5/8” fire code drywall. All gaps, seams and
service penetrations in the ceiling were filled with low rise expanding foam.
See attached photo. The ceiling also has a 6 mil poly vapour barrier. If
anyone has any questions or comments on these building processes I would be
pleased to answer them.
Larry Ryan
Gormley, Ont
lryan@ican.net
Dear
Jacques Rousseau,
I am a designer who currently has my own thoroughly
healthy house under construction here in Santa Barbara. I have done a design
to incorporate not only 'green' practices but use of materials that are
truly healthy to live with. We have used GP's Paperless DensArmor
Plus™ Interior Drywall in the entire house. This may be what the
article referred to as Densglass silver. This drywall can be used in wet
areas instead of regular green board because it does not wick up water. It
also has a fiberglass face which is not productive for mold growth. Those
two features of the product really cut down on the ability to have mold grow
and are why we selected it.
The interior air quality and proximity to materials that
do not detract from healthy well-being were among the greatest priority of
design goals for myself and my family. We have gone to great lengths
including not using any wood or organic materials in the structure or wall
cavities of the whole house. While organics are great to eat, they can grow
bacteria or mold when in walls ;-) Our structure is recycled steel. I am
excited about the DensArmor product and am open to giving tours of my house
for those nearby.
Thanks,
Stephanie Christoff
CHRISTOFF DESIGN
PO Box 21808
Santa Barbara, CA 93121
805-569-1561 Tel
www.christoffdesign.com
 |
Figure 1: Does your air
barrier consistently look like
this? It should !

I HOPE NOT!
|
Membrane laps/seams not
staggered.
Continuity between columns
and roof. Must be work in progress??
Wall preparation, mortar
joints not cleaned.
Primer spilt onto exposed
slab.
Polyethylene not removed on
laps/seams
Dear
Jacques Rousseau,
CMHC's New Best Practice Guide for ElFS:
I am an architect in the
US and teach building technology to architecture students at Cornell
University. I noticed images of a pressure-equalized EIFS cladding system
in a recent article in the
Construction Specifier
(CSI, May 2006, p. 50), and some internet research turned up your name as
CMHC Project Manager on a study of such
systems.
I have always wondered
how introducing pressure-equalization channels behind, or cut into the back
of, the insulation boards is compatible with their function as insulation.
Wouldn't exterior air introduced on the interior side of the insulation
compromise its thermal performance?
I have asked industry
representatives about this and have never received a cogent reply. Do you
have any insight into the question, or can you refer me to anyone who might?
Thanks in advance for
your help.
Jonathan Ochshorn
Associate Professor,
Architecture
phone: 607-255-1194
fax: 607-255-0291
email: jo24@cornell.edu
address: 143 E. Sibley
Hall
Cornell
University
Ithaca, NY
14853
internet:
http://www.people.cornell.edu/pages/jo24
Dear Jonathan ... very good
question!
The channels or the
cavity behind the cladding will not have a great influence on the thermal
performance of the insulation.
For pressure
equalization to occur it requires a very small amount of air (a few %). The
normal pressure in channels or the cavity behind the cladding is at
atmospheric pressure 100 kilopascals, a very strong wind will generate an
equivalent pressure of 1 kilopascal. Therefore the amount of air required
to increase the pressure behind the cladding is very small.
The effect of the
additional air entering the cavity to pressure
equalize the compartment
will be located at the vent hole and should not cause a convective flow.
The effect on the insulation will be localised near the vent hole.
I hope that my
explanation is clear and answers your question.
... Jacques
Dear
Jacques,
Thanks for your answer:
I think I get it. I had a mistaken vision of the channels being more like
the continuous vent spaces above insulation in roof rafters which are
designed such that cold air is encouraged to circulate through the channel.
Instead, these "channels" are more like "chambers" with a single opening
that effectively traps the air, designed to equalize pressure only. The
trapped air basically stays warm (in winter) since only a small amount of
cold "new" air enters to equalize the pressure inside.
As to your other request
about posting on the"Building Envelope Forum" website, I originally intended
to post the question but could not (and still cannot) figure out how to
accomplish that task. I can find no links or instructions on the site.
Feel free to forward this correspondence to someone who can post the
conversation, or let me know how to do it myself.
Again, thanks for your
help.
Jonathan
Dear
Jacques Rousseau,
Do you know of any solution to keep woodpeckers from destroying our brand new EFS and acrylic stucco finish on a multi family building we
have just completed?
Thanks,
Ken
Webster
Kelowna, BC
Day, Kevin [mailto:KDay@halsall.com]
Dear Kevin,
I fake owl is not a bad trick, these shots
are from North Vancouver where Wpeckers can be an issue...
Jacques
Dear
Jacques,
Thanks for the e-mail. We've tried the fake owl in
the past and the woodpeckers seem intelligent enough to figure it out after
a while. However, maybe we'll try again.
Please fell free to post this on your "Forum".
We're open to any advice at this point.
Thanks again,
Ken
Webster
GENERAL
Great news source! Many
thanks for adding me to your mail list.
Arthur Walter, CSI, PSA
Webmaster, Palm Beach Chapter, CSI
Delray Beach, Florida
GENERAL
Dear
Jacques Rousseau,
Thank
you for including me in this forum. I am a licensed Architect in California
working for a consulting group. We have defended developers, general
contractors and subcontractors against allegations with regard to the
construction of large and small buildings. One of our efforts now focuses
on "Peer Review" of projects before they are built. Obviously an open forum
like this will provide useful discussion and ideas as to how we can improve
the built environment.
I look
forward to discussions on issues.
Robert Stowell, AIA
Project Manager
Roel Consulting Group
Dear
Jacques Rousseau,
I
have finally found time to read this forum and it reminds me of the round
tables we used to have at the Alberta Building Envelope Council in the 80s
and not at all surprising to me some of the names I am reading in the
articles were there at the meetings. Keep up the good work!!
Regards:
Jim
Jennings
Manager
Canadian Academy of Building Sciences
Dear
Jacques Rousseau,
Your newsletter sounds great. I have one problem; I am in Texas, where the
heat is usually on the outside Not the inside. Will your newsletter describe
solutions for both cold climate and hot-humid climate situations or at least
differentiate between the two conditions?
Thanks,
Amanda Tullos, Assoc.
AIA, LEED AP
co-Chair
AIA COTE – Houston
American Institute of Architects
Committee on the Environment
http://www.aiahouston.org/cote
Heights Venture
Architects, LLP
1111 North Loop West, Suite 800
Houston, Texas 77008
V 713-869-1103
Direct- 281-854-6111
F 713-869-5573
E
amanda.tullos@hva.cc
www.heightsventure.com
Dear
Jacques Rousseau,
Congratulations on the
Building Envelope Forum. It's awesome!!!
If it's of value to
you, I would be pleased to put a free ad/announcement for it in one of my
future BCBuilding.info newsletter issues. My little ol' rag now goes to over
800 building industry subscribers, most of which are here in B.C.I think
your site/newsletter would be an excellent resource for at least some of
them. Let me know if this is of interest to you, and I'll do what I can to
make it work.
Have a Top Drawer day.
Ken :o)
Ken Farrish
BCBuilding.info
E-mail: ken@bcbuilding.info
Phone: 604-943-9299
Web site: www.bcbuilding.info
A free e-mail newsletter on building technology.
Written for the British Columbia building industry.
Dear
Jacques Rousseau,
Recently I received an
email announcing your Building Envelope Forum newsletter. Considering your
position as publisher and profession as civil engineer, I find it surprising
that the newsletter thus far ignores grading and drainage, site design and
circulation, and landscape architecture. As you know, these design
components are integral to a comprehensive design package.
You may have familiarity
with the Whole Building Design Guide website (http://www.wbdg.org).
Again, a similar issue with primary consideration for the building alone.
The website publishers are currently working to include "whole site" aspects
as part of their website articles and references. I would urge you to
consider the same action.
In my opinion, the
inclusion of planning, landscape architecture and civil engineering into the
various aspects of building function and siting, sustainability, and other
site/building life-cycle considerations and costs would greatly benefit your
newsletter subscribers.
Respectfully,
Amy Baquial
Amy E. Baquial, RLA,
ASLA, LEED AP
Sr. Landscape Architect
Naval Facilities Engineering Command
Southwest Division
1220 Pacific Hwy, Code CI5
San Diego, CA 92132
Phone: (619) 532-1523, Fax -1195 DSN 522-
Email: Amy.Baquial@navy.mil
Dear
Jacques Rousseau,
Colleagues at the
Boundary Layer Wind Tunnel Laboratory at Western recently passed along your
email about the first issue of the Building Envelope Forum. Congratulations,
it is topical and does look very interesting. How does one subscribe to it,
please?
I don't know if you've
heard about our "Three Little Pigs" project. We are in the process of
constructing a $7 M facility to be able to subject full-scale houses and
light frame construction to time- and spatially varying loads that
accurately simulate the turbulent wind. Our facility will also offer the
opportunity to do building science research -- moisture penetration through
walls that may have been damaged by simulated extreme wind loads, for
example. We will also be researching the development and growth of mould.
You can find out more
about our facility and research objectives from our
website:
http://www.eng.uwo.ca/research/ttlpp/
You know...after 30
years in this business, I had a bit of an epiphany yesterday.
I was on site at CFB
Borden with my old friend Gerry Gardiner of Defense Construction, and we
were there for a "deficiency" inspection of one of our Projects.
For me, deficiencies
have always been the bane of my existence...not because I have more than my
share of them, but because here, at the end of a job, no matter how well the
Project has gone, you actually spend time picking it apart to find out what
is wrong or "deficient" in how it has been done. It is always so negative.
Even the word
"deficiency" is negative in its connotation. Yesterday, Gerry decided to
call it something else...he called it "Quality Control". For me, it was like
the difference between saying..."that's a bad kid" and "that kid has bad
habits" We are all in this game to produce something of lasting value.
Instituting Quality Controls, rather than Deficiency Lists sure makes a lot
of sense to me.
It's a little
difference, but I think it is a positive one.
Regards,
Brian Shedden, BSSO
V.P. Client Services
Office Tel:
416-431-7770 ext. 25
Office Fax: 416-431-4335
Cell: 416-991-1083
Dear
Jacques Rousseau
(and Luis),
I would really like to see an editorial discussion in your Forum on the
issue of the Poly vapour barrier that we normally install in walls. This
vapour barrier is seen in the multitude of CMHC Best Practice Guides on Wood
Frame and Steel Stud Insulated construction, and is also still a code
requirement.
I recently attended a presentation by Joe Lstiburek and my colleague John
Straube, emphasizing to my students the prevailing laws of physics that
would seem to indicate that we should not use poly vapour barriers as it
traps the moisture inside the insulation and is the root cause of mold and
rot. It also presented quite a different wall section for frame
construction, that relied much more on rigid cavity insulation, to the point
of excluding batt insulation in some cavities since it would cause
convection currents anyway due to poor installation practices, and end up
wet in the long run.
http://www.buildingscience.com/resources/walls/Vapor_Barriers_Wall_Design.pdf
Where this construction type makes full sense for concrete block walls with
brick veneer (type normally used in commercial and industrial types with
lower insulation code requirements), it is difficult to implement in
residential construction. The amount of rigid cavity placed insulation
required to meet code, without the use of batt insulation in the wall is
very high. You need much stronger brick ties to create the space and this
also affects the foundation detail. Most residential foundations are simply
not wide enough to hold the brick veneer, large gap for rigid and the sill
plate.
As a professor of architecture and building construction and building
science I am totally perplexed as to what I am to teach!
Firstly, I have mostly students in the 18 to 19 year old range, right from
high school, in my class. I am not sure that they are up to understanding
the fine points between the issues, nor prepared to take on the building
inspector or building officials should they try to get a permit and build
without installing a vapour barrier.
Secondly, as an accredited program that is supposed to be sending out
students that know the rules and how to do things properly, this puts me in
an awkward position.
Thirdly, I am not sure what the law says if an Architect decided not to
install one, which is still required by code, and runs into trouble down the
road. Mind you, I am sure that whatever you do, you are damned in this case.
Fourthly, is the code (and the full range of CMHC Best Practice Guides)
ready to implement this change in vapour barrier use for frame construction?
Fifthly, sigh.
thanks
Terri Meyer Boake BES BArch MArch LEED AP
Associate Professor
School of Architecture
University of Waterloo
Dear
Jacques Rousseau,
I
first wish to thank you for your excellent work and informative
newsletters. Next, I wish to pass along a Green tip to include in your next
update of the publication entitled “Farewell to Cockroaches” 60948 or
61145. My tip consists of a bait recipe that I have found to be cheap, very
effective, easy to make, and long lasting. To wit,
·
Buy a one
pound container of Mr. Roach Killer, BoraDust, or Roach Proof (all 99%+
boric acid).
·
Buy a
small can of Eagle sweetened, condensed milk or equivalent
·
Wear a
simple dust mask
·
Mix the
two ingredients in any bowl to a dough like consistency
·
Form dough
balls or small flattened patties and leave to dry on a piece of foil or wax
paper, they harden in a few hours
·
Carefully
wash your hands and the bowl
·
Place them
in roach, silverfish, ant territory like behind the freezer, lay them on top
of the ducts in the basement, stand at the attic hatch and toss them around
in the attic, slide one under the water heater, or pull out a bottom drawer
in the kitchen and lob them over the back to lay on the floor under the
cabinets, etc – the patties fit into thin places and the balls lend
themselves to being rolled into hard to reach spots
·
The left
over bait can then be placed in a clearly labeled zip lock bag and stored
for years in the freezer
·
The bugs
love the sugar and protein of the sweetened condensed milk and feed it to
the colony
·
They never
figure out its poison and never develop an immunity to the boric acid
Why
pay the high cost for commercial bait when any bachelor can make this
inexpensive recipe?
Yours,
Doug Garrett, CEM
President
Building Performance & Comfort, Inc.
PS
– Hope to see you at Joe’s this summer and Happy Holidays to you and yours
from warm Austin, Texas!
Dear
Jacques Rousseau,
Tin can by the sea. I
like it.
You said:
'We would appreciate any
suggestions for topics and speakers that you would recommend'
I would love to speak in
Toronto on the frustrated market in Britain for high performance
manufactured Canadian housing, and how despite a dilapidating and aged
British building stock, a booming property market, household demand, and
plenty of land, it is the planning system here that works against a steady
order stream.
I'm a co-author of 'Why
is construction so backward?' (Wiley 2004)
Regards
YRM
Ian Abley
iabley@yrm.co.uk
http://www.yrm.co.uk
YRM ARCHITECTS
32 York Way London N1
9AB
t:
020 7014 4300 f: 020 7014 4301 yrm@yrm.co.uk
www.yrm.co.uk
YRM Limited. Incorporated in England and Wales No 3335485. Registered at
the above address.
Bill,
Am I right in assuming your
the co-author of the Inuvik Hospital case study cited below?
This email came "out of the
blue" from Jacques Rousseau "Somewhere in Mexico".
Do you know if this is all
valid stuff?
Thanks,
Don Worrall
Executive Director
NWT Construction Association
Jacques Rousseau has been
working with building physics and envelopes for over 35 years and is
well-respected in construction circles. He retired from CMHC last year and
operates the building envelope website from either his Mexico part-year
residence (winter) or from eastern Canada in summer. I believe
“tin-can-by-the sea” may refer to a type of dwelling, perhaps a metal
skinned modular house, but I am not sure of that.
The articles are submitted
from various sources and I take them to be considered expert opinion from
the authors, many of whose work I know. Jacques Rousseau runs quality
control on the articles so they conform to currently accepted practice.
Richard Ogle and I
developed the Inuvik hospital report for presentation to the Canadian Civil
Engineering Society two years ago in June. I have e-mailed Jacques to get
my name re-inserted along with Richard’s into the article posted on the web
site, so Richard does not need to take any of the flack all by himself.
Regards,
Bill
-----Original Message-----
From: Maria.Spinu /unix [mailto:Maria.Spinu@usa.dupont.com]
Sent: January 13, 2006 8:47 AM
To:
richard /unix; Bill Wyness /YK /PWS
Subject: Your case study article
To:
Richard Ogle and Bill Wyness
Dear
Richard and Bill,
I
work for DuPont Building Innovation in Wilmington, Delaware, and I am the
Building Science Integration manager. I have recently read your article on
"Building Air Barrier Testing and Verification
Using Smoke Flow Testing and Infrared Thermography in the Canadian Arctic: A
Case Study - 2002-2003" which was published in the Building Envelope Forum.
I
have a 2-part follow-up/question:
1.
Has it been any follow-up on the building energy performance after repair?
This would be extremely valuable for the industry, since there is no
"before" and "after" documented performance to support the importance of
building airtightness. You might be familiar with the
current effort led by Wagdy Anis, AIA, an architect with Shepley Bulfinch
Richardson and Abbott in Boston, and ABAA (Air barrier association of
America); they have been trying to introduce a code requirement for
airtight buildings in the US. However, there is resistance from some
building trades or building professionals, because there are no documented
cases of improved energy performance by making buildings airtight;
extensive energy modeling done at NIST (in support of this proposal)
clearly support improved energy performance of airtight buildings, but
engineers want to see real data. Your case study would be excellent to
provide this type of documentation. If there hasn't been a follow-up, would
it be difficult to at least get some information on the energy bills before
and after?
2.
If you are doing a similar project in the future Tyvek(R) would like to get
involved. Using a continuous air barrier is an easier and more durable
solution for the building airtightness, and we would love to get some
documentation on specific case studies.
Please do not hesitate to contact me either on the phone or email, if you
have any information or are interested to work with us on future projects.
Regards,
Maria
Maria.Spinu@usa.dupont.com
(302) 999-2839 (W)
(302) 999-4763 (Fax)
(302) 545-0980 (cell)
Bill Wyness NWTAA
Sr. Technical Officer -
Architectural/Structural
Technical
Support Services - Asset Management Division
Public Works & Services -
GNWT
5009 49 St., SMH 3,
Yellowknife NT X1A 2L9
867 873 7847 Fax 867 873
0226
mailto:Bill_Wyness@gov.nt.ca
To: Maria Spinu – Dupont
Building Innovation
Maria - Thanks for your
interest and note.
Comment 1)
The building in the case
study was coming out of construction. As such, it had no long-term
documented operating cost history prior to the remedial work on the
envelope; therefore we have no comparative base for before and after.
Additionally, we recognize
that inexact operational parameters for ventilation in the high arctic can
mask the benefits of a tight envelope, because of the high heating cost of
bringing in normally very cold air, particularly with the air change rates
mandated in a health care facility. Consider Fairbanks as a climate
equivalent for the winter operational model of the Inuvik hospital.
The primary envelope
tightness benefit in this building is considered to be the stable interior
airshed created by effective control of infiltration and exfiltration. The
summer environment in Inuvik can be dusty, encouraging tighter envelopes and
better air filtration at the envelope perimeter and at outside air intakes.
We positively pressurize this class of building (15 Pa or so in this case)
to offset infiltration, so leakage is a primary consideration, because it
generates condensate and frost building up in the envelope air channels.
I am familiar with the NIST
comparative theoretical models, and believe the benefits of a tight envelope
are becoming more universally recognized as fuel costs increase. The
European Union has instigated building energy performance standards starting
in 2006, and, in Canada, Natural Resources Canada has for many years
sponsored energy conservation in buildings through the Commercial Building
Inventive Program (CBIP) which subsidizes sensitivity analysis during design
to maximize return on energy conserving components and systems in buildings.
A way to get comparative
data from the IRHSSC study would be to estimate the envelope leakage rates
of the building before and after remediation, based on calculated
exfiltration volumes. My personal sense is we reduced the exfiltration rate
by about 65%, because we did not seal all the leakage paths found by the
thermographic surveying. (Richard Ogle may have another view of this, so I
speak only for my self).
With this in mind, it is
possible to do energy models (Eg DOE 2, EE4) with the two exfiltration rates
(envelope air ex/infiltration comparison) and with the degree heating days
prevailing in Inuvik (about 11,000 Celsius degree heating days), holding
other variables constant, and see the theoretical energy consumption
variance.
Comment 2)
We recognize the air-barrier
qualities of the various Dupont products and how they are effective in
certain classes of construction. The air barrier system in a structurally
insulated panel system such as was used on the IRHSSC does not lend itself
to using Tyvek, because in Canada the National Building Code requires air
barrier components to be mechanically supported sufficiently to withstand
structural loads (such as wind gusting) which may impinge upon them. Tyvek
is commonly used when construction configurations (wood frame, for instance)
can provide the required structural support for the air-barrier component,
but does not traditionally readily lend itself for application in
non-combustible steel framed construction.
Our Section has examined the
newer self-adhering and dimensionally flexible Tyvek variants; we have
examined them here in the past 2-1/2 years and recognize they have
application where they can be adhered to substrates and not de-bond over
time. The adhesive bed of a peel and stick membrane creates a vapour barrier
in the same plane, and that effect must be considered when positioning the
air barrier in the thermal gradient of the building envelope. The majority
of our communities have low annual mean temperatures and short construction
season, making the application of self-adhering (peel and stick) air barrier
materials problematic because of adhered frost, and low temperatures at
construction sites.
We recommend in GNWT
buildings hot applied (torch bonded) air barriers for the building envelopes
in the cold northern climate, and highly impermeable materials, so the air
and vapour barrier are in the same plane and positioned within the warmer
portion of the envelope, with thermal insulation outboard of this plane.
This is the building physics solution for a cold-climate building, and would
not necessarily be appropriate for a warm climate or humid climate building.
Please feel free to review
“Good Building Practice for Northern Facilities”, available at the GNWT
Public Works and Services web page at
http://www.pws.gov.nt.ca/pdf/GBP/GBP%20home.pdf. That Year 2000 version is
currently outdated in some areas, and is under revision, containing
recommended best practices for building envelopes.
Your attention to Building
Envelope Forum is much appreciated, and I hope you can provide any comments
to Jacques Rousseau, who has been instrumental in establishing that forum
for dialogue.
Please feel free to contact
me if any additional information is needed.
Sincerely,
Bill Wyness NWTAA
Sr. Technical Officer -
Architectural/Structural
Technical
Support Services - Asset Management Division
Public Works & Services -
GNWT
5009 49 St., SMH 3,
Yellowknife NT X1A 2L9
867 873 7847 Fax 867 873
0226
mailto:Bill_Wyness@gov.nt.ca
INTERIOR DAMPPROOFING OF BASEMENT WALLS
Ken,
Interesting
article. I have recently been asked to comment on a 50yr old house in
Toronto with regards to insulating the basement walls. I was hoping to get
your thoughts on the matter.
The
basement has never been finished (only paint) or insulated. The foundation
walls consist of brick masonry. The lower few feet of the foundation wall
are always damp and "look wet". We cannot access the exterior of the walls
to install a proper drainage layer and insulation. The first floor wood
joists frame into the solid masonry walls. The existing basement floor
(slab on grade) is being removed. There is a thought of installing an
interior weep tile below the new basement floor slab. I believe that the
foundation wall should not be insulated as this will reduce the drying
potential of the wall and increase its moisture content. I am suggesting
that an interior drainage layer is installed against the full height of the
foundation wall (that dimpled layer that is commonly used on the exterior of
foundations). This layer will serve to isolate the new interior finishes
from moisture, and also function as a vapour barrier. The bottom of the
drainage layer can be made to connect to the new weep tile (should we be
worried about gases?).
Your
thoughts would be greatly appreciated.
Regards,
Paul Pasqualini
Hi Paul,
I’m going
to pass on a copy of my reply to Jacques Rousseau, editor of the newsletter
who can review my observations and perhaps refer you to someone with more
background in solving these kinds of problems.
If the
problem were mine, I think I’d consider doing the following (accepting that
access to the exterior is not possible and that the floor slab is going to
be removed in any case):
1.
Install a perimeter run of perforated pipe (protected by a geotextile
‘sock’) just inside the footing so that the top of the pipe is at or below
the elevation of the base of the footing;
2.
Connect the perimeter run to the exterior side of the foundation at
intervals with perforated pipe (tunnel beneath the footing). Protect the
pipe including its open end with geotextile ‘sock’.
3.
Connect the perimeter run, with perforated pipe (in a ‘sock’) to a
sump (or the storm sewer if it’s permitted);
4.
Spread 6 inches or so of coarse granular fill over the floor to the
top of the footings (0.15 mm poly over the granular fill would be a good
idea, but care in placing and finishing the new concrete slab will be
required);
5.
Install the interior drainage layer as you suggest, but only from the
top of the new floor slab to the elevation of the exterior grade;
6.
Place the new floor slab;
7.
Repair any obvious cracks or mortar gaps in the wall;
8.
Frame the walls and insulate to a couple of feet below grade—install
0.15 mm poly over the insulated portion.
And the
usual:
9.
Make sure eavestroughs and downspouts are installed and lead water
away from the foundation;
10.
Seal any cracks where paved driveway or walkways abut the foundation;
and
11.
Slope grade away from the foundation.
I think
that, even with the insulation, moisture will continue to wick to the upper
portion of the wall and be able to leave toward the exterior. Hopefully the
moisture load will be reduced by some of the sealing and drainage measures.
Hopefully the exterior of the foundation will not be painted or otherwise
face-sealed to inhibit escape of water vapour (not likely paint would stay
in place anyway). Poly beneath the slab will inhibit soil gas
entry—including water vapour. Good luck!
Ken Rauch
I
will suggest a minor change in the title for the discussion of Code Issues:
Ice Hotel in need of sprinklers as desperate guests need warming - but are
they legal?
Anne
Anne Lewison, AIA
Downtown Design Partnership
7
Hanover Square/ 18th Floor
New
York, NY 10004
FLAT ROOF OR WALL IS THERE A DIFFERENCE
Letter
by George Torok, B.Tech.(Arch.Sci.), Project Manager / Technical Specialist,
Gerald R. Genge Building Consultants Inc., Newmarket, Ontario, Canada.
In response to your question, “Flat roof or wall, is there a
difference?” let me respond by saying that of course, there is a
difference. The difference is set out in the second paragraph of your
article: flat roofs are “expected to be watertight, perhaps even to the
point of allowing ponding water to stand for a short period of time…”
Certainly some components of walls need to be watertight (through-wall
flashings, for example) but we don’t expect walls to resist “ponded” water
over their entire surface (although in the wake of Hurricane Katrina,
undoubtedly there are many people in New Orleans who wish otherwise). This
fundamental difference is well reflected in the requirements of the NBCC,
including the article you cite.
NBCC Article 9.25.1.2 describes general principles of Heat
Transfer, Air Leakage and Condensation Control (the title of Section 9.25).
Your paraphrasing of the requirements of 9.25.1.2 is incomplete and
therefore, your interpretation is flawed. There are three (3) requirements
for the location of “sheet or panel type materials with an air leakage
characteristic less than 0.1 L/(s·m2)
at 75 Pa and water vapour permeance less than 60 ng/ (Pa·s·m2)”,
as follows (paraphrased, to simplify the gobbledygook):
a)
the material
shall be installed on the warm side of the material;
b)
the material
may be installed within the thickness of the thermal insulation, in
accordance with Table 9.25.1.2; or
c)
the material
shall be installed outboard of an air space that is vented to the outdoors,
and for walls, drained.
Appendix A of the NBCC for this article describes the
theoretical background for these requirements. The intent is to “avoid
moisture accumulation” within the assembly due to air leakage and water
vapour diffusion from the warm, humid air from within the building to the
exterior, through the assembly. Provided that the vapour barrier in a
“conventional” flat roof assembly does this (and it certainly can), the
construction is not at variance with the requirements of Article 9.25.1.2.
In this context, the discussion from the NBCC User’s Guide quoted later in
your article does not contradict the requirements of Article 9.25.1.2.
Conventional flat roofs, like other types of roof assembly or
wall assembly, can work very well and provide many years of service,
provided they are constructed in a manner appropriate for the service
environment. That’s the key. Kirby Garden figured that out in 1969
(CBD 120). Unfortunately, this is often forgotten and we do silly things
like try to build face-sealed wall and roof assemblies (like the
conventional flat roofs considered in your article) in the BC rainforest
(where you practice) when other types of wall or roof may be more
appropriate, such as the inverted or protected membrane roof systems and
“rainscreen” wall assembly described in your article. A face-sealed wall
assembly, if built with care, can provide many years of good service in the
Prairie Provinces and even here, in Ontario (where I practice).
I encourage you to download the public review draft of
revisions to CSA-A440.4, Window, Door and Skylight Installation. The
committee, of which I was a part, struggled with the notion of the
appropriateness of installation details in different climatic regions of
Canada. Early in our deliberations, there was a strong push to adopt
“rainscreen” technology as the only way to prepare the rough opening space
around a window product, but the threat of riot from our colleagues from the
dry Prairies (John Ink of CWD Windows and Doors and Dennis Little of New
Home Warranty Program Alberta in particular) and gentle prodding by Adaire
Chown of NRCC (who reminded us that the NBCC does not mandate the
“rainscreen” approach and therefore, a standard cited by the NBCC could not,
either) swayed the committee that another, more flexible approach was
necessary. The solution came from committee member Brian Hubbs and his
colleagues at RDH in Vancouver, using the “Moisture Index” system of
classifying severity of wetting developed at IRC / NRCC and adding modifiers
for exposure and protection. A nomograph for selection of appropriate rough
opening constructions to address Moisture index, exposure and protection was
developed and has been included in Appendix A of the public review draft of
CSA-A440.4 standard, together with descriptions of appropriate rough opening
treatments and some amazing construction details (intended for guidance)
developed by RDH. The concept behind this – selection of construction
appropriate for the service environment – is what you failed to
consider in your argument that the universally most appropriate roof system
is an inverted, or protected membrane, assembly, and that similarly, the
universally most appropriate wall system is a “rainscreen” assembly. Don’t
get me wrong, these are good, systems, and they probably will work in any
service environment, but other assemblies may provide reasonable service
also.
“Reasonable service?” I hear you ask. By that I mean that
any roof or wall assembly, in addition to meeting the technical requirements
of environmental separation, must also be economically feasible for the
purchaser of it. A face-sealed wall assembly in Vancouver with no roof
overhang would be outright foolish technically, forcing a “rainscreen”
approach; however, a face-sealed assembly in Toronto (or on the dry
Prairies) with no roof overhang (most high-rise residential condos, for
example) can work just fine. A “rainscreen” approach in Toronto could be
adopted in lieu of a face-sealed approach, but it would cost more; the
question that must be asked is if the purchaser can afford it at the time.
I’ve heard the argument that a face-sealed assembly may require more
frequent future maintenance, and if such costs are considered at the time of
construction, the “true” capital cost of a face-sealed system may be higher
than a “rainscreen” system. However, if the purchaser cannot afford the
technology at the time, a simpler face-sealed approach may be more
appropriate provided that the future maintenance cost can also be afforded.
Again, in Vancouver this would be foolish but elsewhere where the climate is
different, more flexibility may be possible.
George Torok is a Project Manager and Technical Specialist
with Gerald R. Genge Building Consultants Inc. in Newmarket, Ontario. He
has 18 years experience in the diagnosis and repair of building envelope
performance failures, with special emphasis on glazing systems including
windows, skylights, curtain walls, and insulating glass units. George may
be reached at 1-800-838-8183 or at gtorok@grgbuilding.com.
REPLY
BY GARY JOHNSON
It never fails to amaze
me the extent that people will go to justify the old traditional methods of
construction. I sit on the Standing Committee for Part 5 and have had this
argument many times and hear the same rational - it has worked in some areas
under some conditions so why change. (I'm sure one of the reasons the NRC
is resistant to change is that they would be embarrassed to admit that their
promotion of poly vapour barriers over the years has been a mistake.)
Mr.Torok makes this same
point when he states " Conventional flat roofs . . . can provide many years
of service, provided they are constructed in a manner appropriate for the
service environment." There have been a number of attempts at
quantifying the service environment including the IRC/NRCC Moisture Index
and Joe Lstiburek's map of North America which, I suggest, just muddies the
water, if you will forgive the pun. We seem to stand on our head trying to
make the old systems work. A good example of just how ridiculous this can
get is found in the CMHC Technical e-Newsletter 2005-09-19 article on a test
of a "Dynamic Buffer Zone" approach to a brick veneer/steel stud assembly.
Perhaps I was not
sufficiently clear about the importance of the continuity of the air barrier
in my article. I contend that the air barrier defines the envelope (the
argument will be presented in a future edition of the BE Forum I believe).
I was not promoting the use of a rain screen per say, it is just that a rain
screen is a natural result of the argument. Given this fact (contentious
I'm sure) then the approach to envelope assemblies becomes very straight
forward, applicable to all conditions and, last but not least, almost idiot
proof. Once we get accustomed to building in this manner cost (both initial
and life cycle) will drop.
We could go back to
building the way we did before 1975 - nice and leaky (drafty) with little
insulation that ensured that assemblies dried out soon after they got wet.
Today's requirements for low energy consumption and high expectations for
comfort demand a good air barrier and that requires that the air barrier be
understood (it is not a vapour barrier).
To get back to the
roof/wall discussion I find that many designers do not consider where the
plane of the air barrier is in a roof assembly. Is it the roof membrane on
top of a conventional assembly or the "vapour barrier" on the bottom of the
assembly? To what and how does one connect the wall air barrier? Mr. Torok
seems to be of the opinion that the vapour barrier will perform this
function. Certainly it will, provided it is a material that will seal
around penetrations and take air pressure differential, but then we are
talking about a good membrane so why put another membrane over it? Poly
full of holes from mechanical fasteners for insulation is not the best of
air barriers. (I can hear the argument now - but air can't move it through
it because of all the material on top. If that is so then where is the air
barrier, it certainly isn't the poly - which is my point - people don't seem
to understand the concept of air barriers in roofs.) (Another pet peeve of
mine is why would someone put a vapour diffusion barrier over steel deck, if
there is no air movement through the assembly (i.e. an air barrier) then the
steel deck is just as good as poly when it comes to vapour diffusion.)
I would agree that we
can build conventional assemblies that work but it takes a lot of care,
knowledge and attention on the part of the designer, builder and maintenance
personnel to do it right. Why not use a simple assembly that will work in
every environment and that everyone can understand - I might even be out of
a job if that happened.
Gary
F. Johnson
Building Envelope Specialist
Read Jones Christofferson Ltd.
220, 645 Tyee Road
Victoria, BC
V9A 6X5
Ph: (250) 386-7794
Fax: (250) 381-7900
gjohnson@rjc.ca
REPLY
BY Bill Wyness
Hi George -
I read your letter to the
Editor at Building Envelope Forum, and felt urged to advise that the service
environment of “the prairies” is not always as dry as might be inferred.
I used to sit in lectures at
UBC when Gus, Kirby and others from the old DBR group came out to the B.C.
coast in the '60's and promoted the building physics deployment in that
province. I still have the original CBD binder they handed out, and agree
with you a lot of the building science determined in the '60's and the '70's
was almost lost in the '80's and the '90's in Canada.
I grew up and trained in the
“rainforest” of the B.C. lower mainland and the rainscreen back-vented
pressure equalized style of cladding was a natural consequence of the
construction technology on the west coast, where wood was cheap and a normal
cladding of choice, and exterior stucco (the primordial face-sealed
wood-frame construction cladding) only started appearing en-masse after WWII
with the huge VLA tract housing developments. And this all worked because
the construction was air-leaky and heating was cheap in the mild coastal
climate.
Then I moved to Alberta and
practiced architecture in Edmonton for 12 years. Having been told the
prairies was “Dry”, I was amazed to see building after building with failed
exterior cladding, no eaves protection, and failed face sealed construction
joints. Apparently the industry did not believe the sideways rain that came
without fail every
June through September in
northern Alberta actually soaked cladding materials and crept into envelope
crevices either through capillary action or through air pressure effects!
Some dry service environment!
Now I live in the NWT, one
of the most diverse and demanding building envelope performance environments
in the world, and have learned some of the beliefs and generalizations about
the performance environment north of 60 are naive at best, and outright
dangerous at their worst.
I would suggest that broad
categorizations of Canadian regions as having generically pre-defined
“service environments” is a risky belief system. A few years back we ended
up cutting off the 30” wide eaves during the renovation of a 1950's era wood
frame two storey building in a MacKenzie valley community where, just by
chance, the “dry” north of 60 service environment has a one day maximum
rainfall of 70 mm, much of it coming sideways with the wind. We tried to
avoid cutting off the eaves, but the eaves were eventually cut off after
all, to meet a design aesthetic, and operating under the belief we “don't
get enough rain in the north to worry about eaves” - and now the inevitable
wetting action on the wall is an ongoing maintenance concern.
Fortunately, there is
renewed recognition of the need to incorporate the impact of microclimatic
on building envelopes, but that can be jeopardized when large
multi-provincial design agencies or national organizations use broad-brush
approaches to envelope design.
My experience tells me we
will all make better envelopes if we recognize the benefits of knowing the
building's microclimate, trends in the microclimate, and apply our proven
building physics technology in that context.
Regards,
Bill Wyness NWTAA, MAIBC
Sr. Technical Officer -
Architectural/Structural
Technical
Support Services - Asset Management Division
Public Works & Services -
GNWT
5009 49 St., SMH 3,
Yellowknife NT X1A 2L9
|