Protection from Precipitation Cladding Provisions for Housing and

Small Buildings in the National Building Code of Canada 2005

By: Ken Rauch

 

Introduction

 

Ask anyone in the industry, except possibly Egyptian pyramid contractors, to identify public enemy #1 for environmental separators, and the answer will probably be MOISTURE. Prior to the 1970s energy crisis, when we began superinsulating any cavity that stood between us and outside, the National Building Code of Canada (NBC) devoted more ink to protection from precipitation than combating air leakage and interstitial condensation. Since that time, and as understanding of the mechanisms involved increased, this has been turning around. However, rain continues to fall, and snow continues to melt, and measures to limit damage or unsafe conditions from precipitation ingress continue to be an important element of the NBC.

Part 9 of the NBC, Housing and Small Buildings, describes acceptable materials, systems and equipment to accomplish a minimum level of performance consistent with user health and safety and utility of these building elements for their intended purposes. Alternative, equivalent solutions have always been permitted by the Code, and the new, objectives-based edition is no exception. A critical aspect of alternatives proposed to the prescriptive provisions of Part 9 is a credible assessment of conformity to the Code’s minimum level of performance.

 

Precipitation Protection in Part 9 of the NBC

 

Precipitation-protection provisions in Division B, Part 9 are grouped  with other provisions relating to specific building systems or functions. Major groups of provisions are to be found in Sections 9.20, “Masonry and Insulating Concrete Form Walls Not in Contact with the Ground”, 9.26. “Roofing”, 9.27. “Cladding” and its related Section, 9.28. “Stucco”. In this article, I’ll concentrate on cladding for wall surfaces.

 

Cladding Provisions in the NBC 2005

 

Cladding provisions in the 2005 edition of the NBC are significantly expanded over previous editions. The new edition is more specific as to acceptable design strategies and assemblies. In the 1995 edition of the NBC, cladding performance requirements were quite simply stated: “Exterior walls shall be protected with cladding, including flashing, trim and other special purpose accessory pieces required for the cladding system being used, to restrict the entry of rain and snow into the wall assembly”. In this area at least, the Code has, at the request of industry, become more prescriptive.

Exterior walls are required to be designed and constructed to:

 

  1. minimize precipitation ingress into the assembly and to prevent its entry into interior space, and

  2. minimize the likelihood of deterioration and reduced performance due to mechanical impact and ultraviolet radiation.

Section 9.27.1. breaks down the wide range of cladding materials into five groups:

  1. lumber, wood shingles, shakes, fibre-cement shingles, planks and sheets, plywood, OSB, waferboard, hardboard, vinyl and aluminum or steel,

  2. Stucco,

  3. masonry,

  4. asphalt shingles and

  5. other cladding materials.

There are extensive subsections devoted to each group and, for all types of cladding, there is the option of compliance with the provisions of Part 5, “Environmental Separation”.

 

Acceptable Cladding System Configurations - Two-Plane Systems

 

For residential buildings, a primary and secondary plane of protection is required, as a high level of performance is expected with, perhaps, minimal maintenance. These planes of protection can comprise siding over a sheathing membrane, which has been a familiar and economical system used in Canada for many years. Also considered to satisfy the requirement for a two-plane system are masonry veneer over wood frame and masonry cavity walls.

 

In geographical areas where climatic conditions favour wetting, but do not promote drying (i.e. lower temperatures and high moisture index), a two-plane system with the addition of a capillary break between the first and second planes is required for all buildings. As we read on, we find that this might not be as onerous a requirement as it seems.

 

There are acceptable variations on these systems, all of which can be classified as open rainscreen assemblies. The capillary break could be created by furring behind the cladding or by a layer of open drainage material. In either case, the space between the first and second planes must be drained to the exterior. Perhaps surprisingly, loosely-attached siding, such as metal or vinyl, over sheathing membrane is deemed to satisfy the requirement for a capillary break. The capillary break is not required—although it is always recommended, if it can be shown that:

 

  1. it isn’t vital to the performance of the system,
  2. the wall or intersecting floors aren’t moisture sensitive,
  3. the wall is a “mass wall” (e.g. cast-in-place concrete) or
  4. the building is an accessory building.

 

The Purpose for a First and Second Plane of Protection

 

The first plane of protection discussed previously comprises cladding, trim, accessories and fasteners designed to minimize passage of rain and snow due to:

 

  1. kinetic energy (e.g. driving rain),
  2. surface tension,
  3. capillarity,
  4. gravity and
  5. air pressure differences.

 

The second plane of protection is a drainage layer, complete with flashing designed to dissipate water, that might pass the first plane, to the exterior. Both planes must be maintained at penetrations and interfaces with other wall assemblies.

 

Face-Sealed Systems – An Exception

 

Cladding systems comprising large sheets or panels with well-sealed joints which effectively reduce air infiltration and control the entry of wind-driven rain are permitted to be installed without a second plane of protection. This provision was originally included in the Code to accommodate mobile homes with lock-seamed metal siding—a system that manufacturers have used for many years. However, this provision might be useful for systems comprising panels with battens at the joints, for example. 

As well, where it can be demonstrated that a sheathing material is at least as impervious to air and water penetration as sheathing membrane, and where its joints are at least as impervious to air and water penetration as the material itself, sheathing membrane (second plane of protection) is not required.

 

Conformity Assessment of Alternative Cladding Materials and Systems

 

Despite its prescriptive nature, Part 9 always offers the opportunity for alternative materials or systems. For designers, builders and manufacturers, alternatives to explicitly-mentioned building materials and systems can offer flexibility of design to suit particular conditions, cost savings and the opportunity to move the technology forward. The sticking point is often determining if proposed alternatives actually will offer equivalent performance to the “tried and true”.

 

Sometimes examination, either at the design stage or on-site can satisfy regulatory authorities as to the “equivalency” of a proposed alternative, but more often a third-party review is required. There are hundreds of materials standards referenced by the NBC, and comparison of a material with the provisions of the appropriate standard by a competent agency can pave the way to hassle-free acceptance on the jobsite.

 

The NBC does not assign responsibility for conformity assessment. This is usually the purview of provincial and territorial governments. Immediately following the Preface to the NBC 2005, is a discussion entitled “Relationship of the NBC to Standards Development and Conformity Assessment”. The following is a listing of some resources available to those responsible for ensuring materials and systems meet the performance requirements of the NBC along with some links to more complete information.

 

  1. Laboratory testing is the backbone of certification, registration, evaluation and qualification systems. The Standards Council of Canada has accredited many organizations as capable of testing building products to specified standards. Click on the following link for a listing of accredited laboratories and the testing for which they are approved: http://palcan.scc.ca/SpecsSearch/TLSearchForm.do.
  2. Certification provides a high level of confidence, including, as it does, physical examination, testing, plant examination, follow-up plant inspections, and issuance of assurance that a product, process or system (including, in some cases, entire buildings) conforms to specified provisions. There are more than a dozen accredited certification organizations including the Canadian Standards Association (CSA) and the Underwriters’ Laboratories of Canada (ULC). Useful information on CSA certification may be found at http://www.csa.ca/consumers/faq/Default.asp?language=english.
  3. Quality Registration Organizations, such as the International Organization for Standardization (ISO) [see http://www.iso.org/iso/en/iso9000-14000/index.html] assess conformity to quality assurance standards. You have probably seen “ISO 9000 Registered” emblazoned on manufacturing facilities.
  4. Qualification of products to a standard and inclusion in a “Qualified Products List”. [e.g. the Canadian General Standards Board (CGSB), http://www.pwgsc.gc.ca/cgsb/prgsrv/certprg/certprg-e.html].

 

For Your Information

Update on Adoption of the 2005 NBC by Provinces and Territories

(Thanks to John Archer of the Canadian Codes Centre)

 

 

BC - complete adoption autumn, 2006

YK - end of 2006

NWT - end of 2006

NT - early 2007

AB – autumn, 2006

SK - end of 2006

MB – April, 2006

ON - end of 2006

QC - 2007

NB - end of 2006

PEI - no plans

NS - very soon

NF - no plans

 

 

Provincial/Territorial Policy Advisory Committee on Codes (PTPACC) Membership List as of September 1, 2006

 

Mr. D.M. Crawford, M.Eng., P.Eng.

Chair, PTPACC

Deputy Fire Marshal

Office of the Fire Marshal

Ministry of the Solicitor General

Place Nouveau, 6th Floor, 5775 Yonge Street

North York, Ontario

M2M 4J1

Mr. J. Vasey

Vice Chair, PTPACC

Director

Building Policy Branch

Ministry of Forests and Range and Minister Responsible for Housing

P.O. Box 9951 Stn Prov Govt

Victoria, British Columbia

V8W 9R3

Mr. D. Brezer, MBA, P.Eng.

Director

Building and Development Branch

Ministry of Municipal Affairs and Housing

777 Bay Street, 2nd Floor

Toronto, Ontario

M5G 2E5

 

Mr. B.E. Clemmensen

Ex Officio – Chair CCBFC

Clemmensen & Associates Limited

17 Oakland Avenue

Toronto, Ontario

M9M 2H9

Mr. R.J. Cormier

Director of Public Safety / Fire Marshal

Nova Scotia Department of Environment and Labour

Office of the Fire Marshal

P.O. Box 697

Halifax, Nova Scotia

B3J 2T8

Mr. W. Fallow, P.Eng.

Ex Officio – Chair PTSPC

Chief Plumbing Inspector

Technical Inspection Services

Department of Public Safety

495A Prospect Street, P.O. Box 6000

Fredericton, New Brunswick

E3B 5H1

 

Mr. T. Hinds

Fire Marshal

Office of the Fire Marshal

Dept. of Community Government & Transportation

Government of Nunavut

P.O. Box 490

Rankin Inlet, Nunavut

X0C 0G0

Mr. D. Hodgins

Fire Commissioner

Ministry of Forests and Range and Minister Responsible for Housing

Office of the Fire Commissioner

PO Box 9491 Stn Prov Govt, 1 - 800 Johnson Street

Victoria, British Columbia

V8W 9N7

Mr. C.L. Jones       

Deputy Fire Commissioner

Office of the Fire Commissioner

Government of Manitoba

508 Norquay Building, 401 York Avenue

Winnipeg, Manitoba

R3C 0P8

Mrs. D. Kelland

Assistant Deputy Minister

Government Services Branch

Department of Government Services & Lands

Confederation Bldg., P.O. Box 8700

St. John's, Newfoundland

A1B 4J6

Mr. D. Kozmen

Director - Consumer and Safety Services

Department of Community Services

Government of Yukon

Box 2703

Whitehorse, Yukon

Y1A 2C6

Mr. R.P. McCullough

Ex Officio – Chair PTSFC

Director, Building and Fire Safety

Corrections and Public Safety

Office of the Fire Commissioner

1855 Victoria Avenue, Suite 310

Regina, Saskatchewan

S4P 3V7

Mr. Ted Ross

Ex Officio – Chair PTSBC

Building Code Coordinator

Public Safety Division

Nova Scotia Environment & Labour

PO Box 697

Halifax, Nova Scotia

B3J 2T8

M. G. Tessier

Directeur

Direction de la normalisation et de la qualification

Régie du bâtiment du Québec

545 Crémazie est, 7ième étage

Montréal, Québec

H2M 2V2

Mr. C.M. Tye

Executive Director, Safety Services Branch

Public Safety Division

Alberta Municipal Affairs

16th Floor, Commerce Place, 10155 - 102 Street

Edmonton Alberta

T5J 4L4

Mr. B. Van Tighem

Fire Marshal

Municipal & Community Affairs

Government of the Northwest Territories

500, 5201 - 50th Avenue

Yellowknife, Northwest Territories

X1A 3S9

Mr. A. Wilkins

Director

Technical Inspection Services

Department of Public Safety

PO Box 6000

Fredericton, New Brunswick

E3B 5H1

Mr. T. Young

Executive Director,

Protection and Emergency Services

Saskatchewan Corrections and Public Safety

100 - 1855 Victoria Avenue

Regina, Saskatchewan

S4P 3V7

Mr. J.W. Archer, MRAIC

Ex Officio – PTPACC Secretary

Canadian Codes Centre

Institute for Research in Construction

National Research Council Canada

1200 Montreal Road, Bldg. M-23A, 2nd Floor

Ottawa, Ontario

K1A 0R6

Mr. D. Bergeron

Ex Officio – NRC Advisor

Director, Codes & Evaluation

Institute for Research in Construction

National Research Council Canada

1200 Montreal Road, Bldg. M-23A, 2nd Floor

Ottawa, Ontario

K1A 0R6

 

 

About the Author

 

Ken Rauch is a building technologist with 23 years of service with Canada Mortgage and Housing Corporation in various technical and building code related positions in Manitoba and at CMHC’s National Office in Ottawa. Since 1997, he has assisted the Canadian Codes Centre, NRC with an Intent Analysis of the requirements National Building Code in preparation for the Objective-Based NBC. He makes his home in Cobourg, Ontario. Ken can be contacted by email at ken.rauch@sympatico.ca

 

 
 
 
 

 

Building Envelope Forum is published by York Communications/MMPI, the owners of  the Construction Law Update News Bulletin, Canadian Apartment Investment Report, and Real Estate Forum. York Communications also produces Canada’s largest expositions and conferences for design, construction, and real estate management professionals including Construct Canada, HomeBuilder & Renovator Expo, Concrete Canada, PM Expo, DesignTrends, RoofTech and the Real Estate Forums. For more details, see our website at www.yorkcommunications.ca.